Thanks for the replies...
the recep is first in the line, the circuit is a dinning room , being converted to an entrance way from the new foyer ( where the new light is being placed ) ,
i ran a new circuit for the foyer but thought i may be pushing the number of devices ,
5 convenience recepticles ,
front lights (200watts) ,
rear entrance lights (120watts) ,
two flourescent closet lights (30watts each)
and the ceiling light/fan (392watts-max) ( the fan addition happened today when the fan box arrived from the saturday hardware store trip.... )
if i est 150 watts to each recept i come up with 1522 which is under the 1800 va for 14 awg - but is was told i had to derate the 1800 to 1440 which puts me over. that is why i inquired about tapping the other circuit.
Any ideas on this derating? Is that required for general lighting and receptacles?
|